好文档 - 专业文书写作范文服务资料分享网站

低电压穿越(LVRT)要求及测试 - 图文

天下 分享 时间: 加入收藏 我要投稿 点赞

Protection specifications保护规格

Protection system settings at wind turbine风电机组保护系统设定值

UNS: operating voltage of WTat

generator side

UNS: 发电机侧的风电机组运行电压

??Undervoltage protection U< = 0,8 UNS, retardation 1,5 s to 2,4 s??低压保护U< = 0.8 UNS, 延时1.5 s 至2.4 s

??To enable fault-ride-through, when fault is in the high-voltage system??当高压系统发生故障时确保低电压穿越

??Undervoltage protection U<< = 0,45 UNS, retardation 0,3 s低压保护U<< = 0.45 UNS, 延时0.3s

??For immediate switching-off, when fault is in the medium voltage system??当中压系统发生故障时能立即切断

??Overvoltage protection U>> = 1,2 UNS, retardation 0,1 s

??For protection of WT equipment,为了保护风电机组设备

过压保护U>> = 1.2 UNS, 延时0.1s

??Overfrequency protection f> = 51,5 Hz and Underfrequency protection f< = 47,5 Hz??高频保护f> = 51.5 Hz 和低频保护f< = 47.5 Hz

??To enable operation over the required frequency range,确保在要求的频率范围内运行

LVRT Workshop Beijing 06./07. January 2009Weck: LVRT requirements and testing

35

低电压穿越(LVRT)要求及测试 - 图文

Protectionspecifications保护规格Protectionsystemsettingsatwindturbine风电机组保护系统设定值UNS:operatingvoltageofWTatgeneratorsideUNS:发电机侧的风电机组运行电压??Undervoltagepr
推荐度:
点击下载文档文档为doc格式
87m2q7hm3l8mqar1rxaq
领取福利

微信扫码领取福利

微信扫码分享