MODULE15

MECHANICAL, PLUMBING& E L E C T R I C A LInternationalDesign Standards

J A N U A R Y 2 0 0 5

Module - 15

Marriott - International

Mechanical, Plumbing & Electrical

A.Mechanical Systems........................................15AB.Plumbing Systems...........................................15BC.Electrical Systems...........................................15C

Module Organization

?This Module is a part of an integrated series of 17 Modules.?Coordination with information from other Modules is required.

?The symbol is used to indicate a Module reference that includes

additional information.

Marriott Confidential and Proprietary InformationThe contents of the Design Standards are confidential and proprietary to Marriott International, Inc. and may not bereproduced, disclosed, distributed or used without the express permission of an authorized representative of Marriott.

Copyright, Marriott International, Inc., unpublished material. All rights reserved.

Contents

January 2005Design Standards - Copyright, Marriott International, Inc.

Marriott Hotel - International

Mechanical - 15A

Module 15 - Part A

Mechanical Systems

Design Standards - Copyright, Marriott International, Inc. January 2005 15A - A

15A - Mechanical

Marriott Hotel - International

Mechanical Systems Table of Contents

Subject...................................................................................Page A. General Requirements.............................................................1 B. Building Cooling / Heating Load Calculations..........................2 C. HVAC System Requirements...................................................3 D. Central Cooling Plant...............................................................5 E. Central Heating Plant...............................................................8 F. Piping Systems......................................................................10 G. Air Side Systems....................................................................13 H. Public and Back-of-House AHUs...........................................16 I. Guestroom / Guest Corridor Fresh-Air AHUs........................18 J. Ductwork................................................................................20 K. Smoke Control System..........................................................23 L. Fuel Oil System......................................................................25 M. Testing and Balancing Services.............................................26 N. Automatic Temperature Controls (ATC) & Building

Management System (BMS)..................................................26 O. Table 15A-1 – Environmental Requirements.........................29

Module Organization

? This Module is a part of an integrated series of 17 Modules. ? Coordination with information from other Modules is required.

? The reference symbol is used to indicate a Module reference that includes additional information.

Marriott Confidential and Proprietary Information The contents of the Design Standards are confidential and proprietary to Marriott International, Inc. and may not be reproduced, disclosed, distributed or used without the express permission of an authorized representative of Marriott.

Copyright, Marriott International, Inc., unpublished material. All rights Reserved

15A - B

January 2005

Design Standards - Copyright, Marriott International, Inc.

Marriott Hotel - International

Mechanical Systems

Mechanical - 15A

A. General Requirements

1. Codes and Standards:

? Information contained in this Module is intended to set

minimum mechanical system requirements and is not intended to provide complete design solutions to project specific situations.

? Comply with the more stringent of governing laws,

applicable governing codes and regulations, and these Design Standards.

? Refer enhancements, deviations, and conflicts between

design standards to Marriott A&C Engineering for resolution.

? FM Global: Fired pressure vessels, boilers, boiler tanks

and their safety trains (controls that include combustion safeguards, safety shut-off valves, over temperature protection and pressure relief valves) are required to be FM Global approved.

2. Building Pressures: Design building to maintain positive

pressure, maintain environmental requirements (temperature and humidity) and ensure guest comfort.

? Minimum outside air intake quantities must exceed

building exhaust quantities by 10%.

? In high-rise buildings, consider \

and the resulting infiltration. The use of entry vestibules, with two sets of double doors will significantly reduce stack effect. See Module <2A> for application of architectural requirements at Lobby entrance.

3. Equipment Selection: Select and provide equipment,

components and specified materials rated for applicable service, environment, temperatures and pressures.

? Install interior designed equipment for inside use only

and not for outside use.

? Design and construct outside equipment for project

specific conditions.

4. Fire Protection / Life Safety: See Module <14>.

5. Environmental Requirements: Design and select

equipment to maintain indoor space temperature and humidity conditions when using ventilation requirements for occupants and internal heat gain in compliance with Table 15A-1 – HVAC Environmental Requirements at end of this document.

6. Dimensions, Sizes and Measurements: In this Standard,

conversions from English to metric (SI) units are approximate. Verify, coordinate and confirm product and material dimensions for required design applications.

Design Standards - Copyright, Marriott International, Inc.

January 2005

15A - 1